A01317 alarm in siemens 6RA80 DC Drive

2 Posts
1 Users
0 Likes
127 Views
Posts: 14731
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : De-activated component again present comes when a component of the target topology for an active drive object is inserted and the associated parameter of the component is set to "de-activate" (p0125, p0145, p0155, p0165).

Note: This is the only message that is displayed for a de-activated component.

Remedy:

The alarm automatically disappears again with the following actions:
- activate the components involved (p0125 = 1, p0145 = 1, p0155 = 1, p0165 = 1).
- again withdraw the components involved.

See also: p0125 (Activate/de-activate power unit components), p0145 (Activate/de-activate encoder interface)

1 Reply
Posts: 14731
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : De-activated component again present. If a component of the target topology for an active drive object is inserted and the associated parameter of the component is set to "de-activate" (p0125, p0145, p0155, p0165).

Note: This is the only message that is displayed for a de-activated component.

Remedy:

The alarm automatically disappears again with the following actions:
- activate the components involved (p0125 = 1, p0145 = 1, p0155 = 1, p0165 = 1).
- again withdraw the components involved.

See also: p0125 (Activate/de-activate power unit components), p0145 (Activate/de-activate encoder interface)