How can resolve problem A2002 OVERVOLTAGE alarm in ABB ACS150 ?

2 Replies
Posts: 14781
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : DC overvoltage controller is active.

Programmable fault function

parameter 1610 - DISPLAY ALARMS

1. Check deceleration time

parameters 2203 - DEC TIME 1 and

2206 - DEC TIME 2.

2. Check input power line for static or transient overvoltage