F0017 UNDERLOAD fault in ABB ACS150

3 Posts
2 Users
0 Likes
234 Views
Posts: 0
Topic starter
Joined: 53 years ago

How can resolve problem F0017 UNDERLOAD fault in ABB ACS150 ?

Topic Tags
2 Replies
Posts: 5227
Admin
(@click2electro)
Member
Joined: 2 years ago

Cause : Motor load is too low due to, for example, release mechanism in driven equipment.

1. Programmable fault function,

parameters 3013...3015.

2. Check for problem in driven equipment.

3. Check fault function parameter settings.

4. Check motor power against drive power.