Forum

Share:
Notifications
Clear all

F1016 PAR USER LOAD C Fault in ABB ACS310 Drive

2 Posts
1 Users
0 Likes
612 Views
Posts: 12619
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

How can resolve problem F1016 PAR USER LOAD C Fault in ABB ACS310 Drive ?

1 Reply
Posts: 12619
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Incorrect user load curve parameter setting.

Check parameter settings. Following must apply:
• 3704 LOAD FREQ 1 < 3707 LOAD FREQ 2 < 3710 LOAD FREQ 3 < 3713 LOAD FREQ 4 < 3716 LOAD FREQ 5
• 3705 LOAD TORQ LOW 1 < 3706 LOAD TORQ HIGH 1
• 3708 LOAD TORQ LOW 2 < 3709 LOAD TORQ HIGH 2
• 3711 LOAD TORQ LOW 3 < 3712 LOAD TORQ HIGH 3
• 3714 LOAD TORQ LOW 4 < 3715 LOAD TORQ HIGH 4
• 3717 LOAD TORQ LOW 5 < 3718 LOAD TORQ HIGH 5.

Reply
Share: