A5013 Alarm in ABB ACS550 Drive

3 Posts
1 Users
0 Likes
504 Views
Posts: 5095
Admin
Topic starter
(@click2electro)
Member
Joined: 2 years ago

How can resolve problem A5013 Alarm in ABB ACS550 Drive ?

Topic Tags
2 Replies
Posts: 5095
Admin
Topic starter
(@click2electro)
Member
Joined: 2 years ago

Button is disabled, because start is inhibited.

set parameter 2108 - 0 (Disables the Start inhibit function.)

 

Reply
Posts: 5095
Admin
Topic starter
(@click2electro)
Member
Joined: 2 years ago

Cause : Button is disabled, because start is inhibited.

set parameter

2108 - 0 (Disables the Start inhibit function.)

1601 - 0 (Disable run enable)

2109 - 0

Sets the Start inhibit function on or off.

If the drive is not actively started and running, the Start inhibit function ignores a pending start command in any of the following situations and a new start command is required.

A fault is reset.
Run Enable (parameter 1601) activates while start command is active.
Mode changes from local to remote.
Control switches from EXT1 to EXT2.
Control switches from EXT2 to EXT1.

 

Reply