A5013 Alarm in ABB ACS550 Drive

5 Posts
2 Users
0 Reactions
3,570 Views
Posts: 18017
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

How can resolve problem A5013 Alarm in ABB ACS550 Drive ?

4 Replies
Posts: 18017
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Button is disabled, because start is inhibited.

set parameter 2108 - 0 (Disables the Start inhibit function.)

 

Reply
Posts: 18017
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Button is disabled, because start is inhibited.

set parameter

2108 - 0 (Disables the Start inhibit function.)

1601 - 0 (Disable run enable)

2109 - 0

Sets the Start inhibit function on or off.

If the drive is not actively started and running, the Start inhibit function ignores a pending start command in any of the following situations and a new start command is required.

A fault is reset.
Run Enable (parameter 1601) activates while start command is active.
Mode changes from local to remote.
Control switches from EXT1 to EXT2.
Control switches from EXT2 to EXT1.

 

Reply
2 Replies
 arun
(@arun)
Joined: 12 months ago

New Member
Posts: 1

parameter 2108 value allready 0 but drive local mod run but fault show 5013 & drive not start

 

Reply
Admin
(@click2electro)
Joined: 3 years ago

Member
Posts: 18017

@arun first take backup on display and then set 9902 - 1

Reply