How can resolve problem F529 M1 field exciter not OK Fault In ABB DCS880 ?

1 Reply
Posts: 14733
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Motor 1 field exciter is not okay. A fault was found during self-
diagnosis of the field exciter or a power failure happened in the
field exciter.

Check:

The field exciter operation. E.g. the field contactor or mains
contactor (in case of an OnBoard field exciter) is not closed
or closing too late.

For fault messages at the field exciter itself (flashing LEDs),
04.26 M1 field exciter fault word and 04.36 M1 field exciter
warning word.