switch on inhibited-supply STO terminal w/24V

2 Posts
2 Users
0 Reactions
352 Views
Posts: 12
 sam
Topic starter
(@sam)
Eminent Member
Joined: 4 months ago
[#20360]

please support on this


1 Reply
Posts: 20042
Admin
(@click2electro)
Member
Joined: 5 years ago

The "Switching on inhibited - STO terminal w/ 24 V (hardware)" fault in Siemens SINAMICS drives typically indicates missing 24V DC on the Safety Terminals (EP+ / STO) on the Power Module. Ensure \(24V\) is applied to EP terminals (e.g., X21:3 and X21:4 on booksize) and that the Control Unit (CU) is properly seated.

Troubleshooting Steps for STO Fault:
  • Check EP Terminals (Power Module): Ensure 24V DC is present at the EP+ and EP- terminals (e.g., X21:3, 4 on PM240-2). Without this, the drive will show this fault even if Safety Integrated is not explicitly configured.
  • Verify Wiring: Check for loose or broken wires in the emergency stop circuit connecting to the drive.
  • Check CU Seating: Ensure the Control Unit (CU) is fully seated and properly connected to the Power Module (PM).
  • Check Parameters: Verify that Safety Integrated functions are correctly parameterized for your application.
  • Voltage Levels: Confirm the 24V supply is stable and not dropping below the threshold