Facing A8526 Fault in siemens g120

2 Posts
2 Users
0 Reactions
757 Views
Posts: 10
Topic starter
(@neeraj)
Eminent Member
Joined: 4 months ago
[#20369]

i have siemens g120 drive and my vfd showing A8526 fault in running condition and after power recycle then drive running fine. Please suggest how to correct this fault.


1 Reply
Posts: 20042
Admin
(@click2electro)
Member
Joined: 5 years ago

Fault A08526 on a Siemens SINAMICS G120 indicates " PROFINET: No cyclic connection," meaning the drive has lost communication with the PLC.

Common causes include incorrect device names, faulty wiring, or a missing connection. Solutions involve verifying PROFINET names, checking cable connections, or disabling the bus protocol (p2030=0) if not using PROFINET


Reply