A149 fault in WEG CFW900 Drive
A149 alarm in WEG CFW900 Drive indicates a Timeout on Modbus TCP. This means the Modbus TCP client stopped sending telegrams to the drive within the configured timeout period.
It indicates that the device stopped receiving valid telegrams for a period longer than the setting in C9.6.3. The time counting starts as soon as it receives the first valid telegram.
  • Check network installation, broken cable or fault/poor contact on the connections with the network, grounding.
  • The Modbus TCP client is not actively sending telegrams to the equipment in a time shorter than the setting in parameter C9.6.3.
Note: This function can be disabled in parameter C9.6.3.
Check connections, cables, and grounding. Ensure the master/client is sending telegrams faster than the timeout configured in parameter C9.6.3, or adjust C9.6.3 to disable the timeout.