F0021 fault in WEG CFW701 Drive indicates a DC Link Undervoltage. This means the internal DC bus voltage has dropped below the safe operating minimum, usually due to an input power dip or phase loss.
The input voltage is too low and the DC link voltage dropped below the minimum permitted value (monitor the parameter P0004):
- Ud < 223 V: For 200 / 240 V three-phase input voltage.
- Ud < 170 V: For 200 / 240 V single-phase input voltage (models CFW701XXXXS2 or CFW701XXXXB2, P0296 = 0).
- Ud < 385 V: For 380 V input voltage (P0296 = 1).
- Ud < 405 V: For 400 / 415 V input voltage (P0296 = 2).
- Ud < 446 V: For 440 / 460 V input voltage (P0296 = 3).
- Ud < 487 V: For 480 V input voltage (P0296 = 4).
- Ud < 530 V: Input voltage 500 / 525 V (P0296 = 5).
- Ud < 580 V: Input voltage 550 / 575 V (P0296 = 6).
- Ud < 605 V: Input voltage 600 V (P0296 = 7).
- Phase loss at the inverter input.
- Pre-charge circuit failure.
- Parameter P0296 was set to a value higher than the power supply rated voltage.
Monitor parameter P0004. Check physical input terminals. Ensure correct configuration of parameter P0296 to match incoming rated mains voltage. Check pre-charge circuit paths.