F249 fault in WEG CFW900 Drive indicates a Timeout on Modbus TCP. This means the Modbus TCP network disconnected or stopped polling, causing the drive to fault on communication loss.
It indicates that the device stopped receiving valid telegrams for a period longer than the setting in C9.6.3.
- Check network installation, broken cable or fault/poor contact on the connections with the network, grounding.
- Ensure the Modbus TCP client always sends telegrams to the equipment in a time shorter than the setting in C9.6.3.
Note: This function can be disabled in parameter C9.6.3.
Check connections, cables, and grounding. Ensure the master/client is sending telegrams faster than the timeout configured in parameter C9.6.3, or adjust C9.6.3 to disable the timeout.