Forum

Share:
Notifications
Clear all

A029 alarm in siemens 6RA70 DC Drive

2 Posts
1 Users
0 Reactions
387 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem A029 alarm in siemens 6RA70 DC Drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Motor overtemperature (active in all operating states)

Selection via

P493=1 or 3 (thermostat at terminals 22 / 23) or

P494=1 or 3 (thermostat at terminals 204 / 205)

When parameter P490.01=1 (KTY84 at terminals 22 / 23) or P490.02=1 (KTY84 at terminals 204 / 205):

The alarm is activated if the motor temperature reaches or exceeds the values set in parameter P492.

When parameter P490.01=2, 3, 4 or 5 (PTC thermistor at terminals 22 / 23) or P490.02=2, 3, 4 or 5 (PTC thermistor at terminals 204 / 205):

The alarm is activated if the motor temperature reaches or exceeds the trip value of the selected PTC.

Reply
Share: