How can resolve problem A032 alarm in siemens 6RA70 DC Drive ?
Cause : SIMOREG CCP not ready (active in operating states of < o4.0)
Possible causes
β’ No voltage at U, V, W terminals of SIMOREG CCP
β’ Voltage at C-D on CCP does not match voltage at C-D on SIMOREG DC-MASTER
β’ Surge absorbing capacitors of SIMOREG CCP have not reached setpoint voltage
β’ Paralleling interface cable is not connected to SIMOREG CCP assigned to paralleling master
β’ No connection between SIMOREG DC-MASTER and SIMOREG CCP via G-SST2 serial interface
β’ No connection between parallel SIMIOREG CCPs
β’ Contents of technical data memory on SIMOREG CCP (MLFB, rated values, serial number) invalid
β’ I2t value of voltage chopper 1 is too high (> 100%)
β’ I2t value of voltage chopper 2 is too high (> 50%)