How can resolve problem A032 alarm in siemens 6RA70 DC Drive ?
Cause : SIMOREG CCP not ready (active in operating states of < o4.0)
Possible causes
• No voltage at U, V, W terminals of SIMOREG CCP
• Voltage at C-D on CCP does not match voltage at C-D on SIMOREG DC-MASTER
• Surge absorbing capacitors of SIMOREG CCP have not reached setpoint voltage
• Paralleling interface cable is not connected to SIMOREG CCP assigned to paralleling master
• No connection between SIMOREG DC-MASTER and SIMOREG CCP via G-SST2 serial interface
• No connection between parallel SIMIOREG CCPs
• Contents of technical data memory on SIMOREG CCP (MLFB, rated values, serial number) invalid
• I2t value of voltage chopper 1 is too high (> 100%)
• I2t value of voltage chopper 2 is too high (> 50%)