How can resolve problem A035 alarm in siemens 6RA70 DC Drive ?
1 Reply
Jun 13, 2022 9:37 am
Cause : Drive blocked (active in operating states of – –, I, II)
The monitoring function responds if the following conditions are fulfilled for longer than the time set in parameter P355:
♦ Positive or negative torque or armature current limit reached
♦ Armature current is greater than 1% of converter rated armature DC current
♦ The actual speed value is less than 0.4% of maximum speed