Forum

Share:
Notifications
Clear all

A037 alarm in siemens 6RA70 DC Drive

2 Posts
1 Users
0 Reactions
135 Views
Posts: 14965
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

How can resolve problem A037 alarm in siemens 6RA70 DC Drive ?

1 Reply
Posts: 14965
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : I2t motor monitor has responded (active in operating states of – –, I, II)

The alarm is activated when the calculated I2t value of the motor reaches the value which corresponds to the final temperature at 100% of permissible continuous motor current (= P113*P100).

Reply
Share: