F001 fault in siemens 6RA70 DC Drive
Cause : Failure of electronics power supply comes when failure of the electronics supply voltage (terminals 5U1, 5W1, 5N1) in “RUN” state for longer than the “restart” time set in parameter P086 or the electronics are operating on undervoltage.
Possible fault causes:
♦ Line contactor has opened in “RUN” state
♦ Brief supply failure
♦ Supply voltage too low
Cause : Failure of electronics power supply. Failure of the electronics supply voltage (terminals 5U1, 5W1, 5N1) in “RUN” state for longer than the “restart” time set in parameter P086 or the electronics are operating on undervoltage.
Electronics supply voltage in “RUN” has been interrupted for longer than setting in P086 - i002 Duration of actual supply failure in 1/10 seconds