F009 fault in siemens 6RA70 DC Drive

2 Posts
1 Users
0 Reactions
282 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Line frequency greater than the maximum line frequency acc. to parameter P364 comes when frequency of armature supply is greater then maximum line frequency.

  • Up to software version 1.7 the threshold for activation of the fault message (maximum line frequency) is 65Hz
  • Frequency of the armature supply > maximum line frequency
  • Frequency of the field supply > maximum line frequency
  • Line frequency greater than the maximum line frequency for longer than set in parameter P086 (if >0)
1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Line frequency greater than the maximum line frequency acc. to parameter P364 (active in operating states of ≤ o5)

1 Frequency of the armature supply > maximum line frequency
2 Frequency of the field supply > maximum line frequency
4 Line frequency greater than the maximum line frequency for longer than set in parameter P086 (if >0)