F012 fault in siemens 6RA70 DC Drive

2 Posts
1 Users
0 Reactions
415 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Telegram failure at GSST1 comes when the receipt of the first valid protocol, no further telegrams have been received within the time period set in parameter P787.

Possible fault causes

• Cable break
• Error in USS master

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Telegram failure at GSST2 when P790 = 2:

USS telegram failure at G-SST2
(active from the first receipt of a valid protocol in all operating states)

After the receipt of the first valid protocol, no further telegrams have been received within the time period set in parameter P797.

Possible fault causes
Cable break
Error in USS master
when P790 = 4 or 5: Peer-to-peer telegram failure at G-SST2
(active in operating states of o6)

After the receipt of the first valid protocol, no further telegrams have been received within the time period set in parameter P797.

Possible fault causes
Interruption in connecting cable
EMC interference on connecting cable
P797 is set too low

Reply