F013 fault in siemens 6RA70 DC Drive

2 Posts
1 Users
0 Reactions
181 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Telegram failure at GSST3 comes when the receipt of the first valid protocol, no further telegrams have been received within the time period set in parameter P807.

  • USS telegram failure to G-SST3 (active from the first receipt of a valid protocol in all operating states) 

Possible fault causes:

  • Cable break
  • Error in USS master
  • Interruption in connecting cable
  • EMC interference on connecting cable
  • P807 is set too low

    when P800 = 4 or 5: Peer-to-peer telegram failure at G-SST3 (active in operating states of ≤ o6)

  •  
1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Telegram failure at GSST3 when P800 = 2:

USS telegram failure to G-SST3
(active from the first receipt of a valid protocol in all operating states)

After the receipt of the first valid protocol, no further telegrams have been received within the time period set in parameter P807.

Possible fault causes
Cable break
Error in USS master

when P800 = 4 or 5: Peer-to-peer telegram failure at G-SST3 (active in operating states of o6)

After the receipt of the first valid protocol, no further telegrams have been received within the time period set in parameter P807.

Possible fault causes
Interruption in connecting cable
EMC interference on connecting cable
P807 is set too low

Reply