F015 fault in siemens 6RA70 DC Drive

2 Posts
1 Users
0 Reactions
384 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem F015 fault in siemens 6RA70 DC Drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Telegram failure on one SIMOLINK board (active when U741 > 0 as soon as the first valid telegram is received)

After receipt of one valid telegram, no further valid telegrams have arrived within the period set in parameter U741.

Possible fault causes
Break in connecting cable
Parameter setting change during telegram exchange (for parameters see Section 11 "Configuration of SIMOLINK board)

U741 is set to low
Fault value:
1 Telegram failure on 1 st SLB
2 Reserved