Siemens 6RA70 DC Drive
2
Posts
1
Users
0
Reactions
369
Views
Jun 13, 2022 7:00 am
How can resolve problem F031 fault in siemens 6RA70 DC Drive ?
1 Reply
Jun 13, 2022 7:00 am
Cause : Speed controller monitoring (active in operating states of – –, I, II)
The monitor responds when the difference between the connectors selected in P590 and P591 (factory setting: Setpoint/actual value difference of speed controller) exceeds the limit set in parameter P388 for longer than the time set in parameter P390.
Possible fault causes
• Open control loop
• Controller not optimized
• P590 or P591 is not correctly parameterized