Forum

Share:
Notifications
Clear all

F031 fault in siemens 6RA70 DC Drive

2 Posts
1 Users
0 Reactions
369 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem F031 fault in siemens 6RA70 DC Drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Speed controller monitoring (active in operating states of – –, I, II)

The monitor responds when the difference between the connectors selected in P590 and P591 (factory setting: Setpoint/actual value difference of speed controller) exceeds the limit set in parameter P388 for longer than the time set in parameter P390.

Possible fault causes
Open control loop
Controller not optimized
P590 or P591 is not correctly parameterized

Reply
Share: