How can resolve problem F032 fault in siemens 6RA70 DC Drive ?
1 Reply
Admin
Topic starter
(@click2electro)
Member
Cause : SIMOREG CCP not ready (active in operating states of < o4.0)
Possible error causes
No connection or cable break at X172 (G-SST2)
No connection or cable break at X165 (paralleling interface master) in a parallel connection
No connection or cable break at X29_PAR or X30_PAR (extinction-pulse interface) in a parallel connection
Hardware defective in charging circuit of extinguishing capacitors
Blown fuse in the line-side or motor-side armature circuit
Blown fuse in the precharging circuit for the chopper capacitors
Required cooling phase for chopper resistors still in progress
MLFB (order number) data of the SIMOREG CCP (n570, n571, n572) are invalid or nonexistent