F036 fault in siemens 6RA70 DC Drive

2 Posts
1 Users
0 Reactions
404 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem F036 fault in siemens 6RA70 DC Drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : No armature current is flowing (active in operating states of – –, I, II)

This monitoring function responds if the armature firing angle is at the rectifier stability limit for more than 500 ms and the armature current is less than 1% of the converter rated armature DC current.

Possible fault causes
Armature circuit is open (e.g. DC fuses have blown, open circuit, etc.)
Rectifier stability limit αG (P150) is incorrectly set
Drive is operating at αG limit (e.g. due to supply undervoltage)
EMF is too high because maximum speed setting is too high, refer to P083, P115, P143, P741)
EMF is too high because field weakening is not selected (refer to P082)
EMF is too high because field current is set too high (refer to P102)
EMF is too high because transition speed for field weakening is set too high (refer to P101) ??