How can resolve problem F046 fault in siemens 6RA70 DC Drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Analog select input for main setpoint (terminals 4 and 5) faulty (active in operating states of o6)

This fault message is activated when P700=2 (current input 4 to 20 mA) and an input current of less than 2mA is flowing.

Possible fault causes
Open circuit in supply cable
P700 is incorrectly set