F047 fault in siemens 6RA70 DC Drive

2 Posts
1 Users
0 Reactions
468 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem F047 fault in siemens 6RA70 DC Drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Analog select input 1 (terminals 6 and 7) is faulty (active in operating states of o6)

This fault message is activated when P710=2 (current input 4 to 20 mA) and an input current of less than 2mA is flowing.

Possible fault causes
Open circuit in supply cable
P710 is incorrectly set