How can resolve problem F053 fault in siemens 6RA70 DC Drive ?
1 Reply
Jun 13, 2022 7:37 am
Cause : Fault message from free function block FB288 (active in all operating states)
1 the binector wired via parameter U102 Index.005 is in the state log.”1”
2 the binector wired via parameter U102 Index.006 is in the state log.”1”
3 the binector wired via parameter U102 Index.007 is in the state log.”1”
4 the binector wired via parameter U102 Index.008 is in the state log.”1”