F062 fault in siemens 6RA70 DC Drive

2 Posts
1 Users
0 Reactions
231 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem F062 fault in siemens 6RA70 DC Drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Fault in parameter memory (active in all operating states)

Software monitoring of correct functioning of the EEPROM module (non-volatile memory) on the A7009 board.

The EEPROM values contains all data which must be protected in the case of a power failure (i.e. parameter values and process data which must remain stored during power failures).

The following are monitored:

Connection between the A7001 electronics board and the EEPROM on the A7009 backplane wiring assembly

Whether the parameter values stored on the EEPROM are within the permissible value range

Whether data are being correctly stored on the EEPROM. For this purpose, values are read and checked for correctness after they are transferred to the module

Whether the checksum of the non-volatile process data in the EEPROM is correct

Possible causes for all fault types:

Excessive EMC-related interference is present (e.g. due to unprotected contactors, unscreened cables, loose shield connections)