F062 fault in siemens 6RA70 DC Drive
How can resolve problem F062 fault in siemens 6RA70 DC Drive ?
Cause : Fault in parameter memory (active in all operating states)
Software monitoring of correct functioning of the EEPROM module (non-volatile memory) on the A7009 board.
The EEPROM values contains all data which must be protected in the case of a power failure (i.e. parameter values and process data which must remain stored during power failures).
The following are monitored:
Connection between the A7001 electronics board and the EEPROM on the A7009 backplane wiring assembly
Whether the parameter values stored on the EEPROM are within the permissible value range
Whether data are being correctly stored on the EEPROM. For this purpose, values are read and checked for correctness after they are transferred to the module
Whether the checksum of the non-volatile process data in the EEPROM is correct
Possible causes for all fault types:
Excessive EMC-related interference is present (e.g. due to unprotected contactors, unscreened cables, loose shield connections)