How can resolve problem F067 fault in siemens 6RA70 DC Drive ?
1 Reply
Jun 13, 2022 7:54 am
Cause : Converter cooling faulty (active in operating states of ≤ o13)
The heatsink temperature monitoring function is activated 6s after connection of the electronics supply.
(The current heat sink temperature is indicated at parameter r013 and on connector K050)
Fault value: r047 Index 002 to 016:
1. Heatsink temperature > permissible heatsink temperature (depending on the MLFB) - i002 Measured heatsink temperature (16384 .. 100°C)
2. Heatsink temperature sensor is defective - i003 Measured ADC value
3. Converter fan is defective.