How can resolve problem F067 fault in siemens 6RA70 DC Drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Converter cooling faulty (active in operating states of o13)
The heatsink temperature monitoring function is activated 6s after connection of the electronics supply.

(The current heat sink temperature is indicated at parameter r013 and on connector K050)

Fault value:      r047 Index 002 to 016:

1. Heatsink temperature > permissible heatsink temperature (depending on the MLFB) - i002 Measured heatsink temperature (16384 .. 100°C)

2. Heatsink temperature sensor is defective - i003 Measured ADC value

3. Converter fan is defective.