How can resolve problem F080 fault in siemens 6RA70 DC Drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Error in initialization of a CB/TB board

Possible causes for fault values 1 and 6:
CB/TB board is defective
CB/TB board is not installed correctly
CB/TB board is taking too long to run up (e.g. due to very complex TB configuration)

Fault value (r949 index 001):                r047 index 002 to 016:

1. The "Heartbeat counter“ of the CB/TB has not started to count within 20 s

i015 Code number of board:

1. TB or 1 st CB ,

2. 2 nd CB

2. The product version of the installed CT/TB board is not compatible with the SIMOREG 6RA70 converter

i002 Code number of slot containing incompatible board:
2 Slot D
3 Slot E
4 Slot F
5 Slot G
6 CB when configuration includes TB

5. Parameters P918, U711 to U721 are not correctly set or not accepted after a change by means of U710 = 0 setting. (The meanings of these parameters are defined in the manual for the relevant CB board, see also function diagrams, Section 8, Sheets Z110 and Z111)

i015 Code number of board:
1. TB or 1st CB
2. 2 nd CB

6. The initialization run for a CB/TB board has not been completed within 40 s

i015 Code number of board:
1. TB or 1st CB
2. 2 nd CB