How can resolve problem F080 fault in siemens 6RA70 DC Drive ?
Cause : Error in initialization of a CB/TB board
Possible causes for fault values 1 and 6:
♦ CB/TB board is defective
♦ CB/TB board is not installed correctly
♦ CB/TB board is taking too long to run up (e.g. due to very complex TB configuration)
Fault value (r949 index 001): r047 index 002 to 016:
1. The "Heartbeat counter“ of the CB/TB has not started to count within 20 s
i015 Code number of board:
1. TB or 1 st CB ,
2. 2 nd CB
2. The product version of the installed CT/TB board is not compatible with the SIMOREG 6RA70 converter
i002 Code number of slot containing incompatible board:
2 Slot D
3 Slot E
4 Slot F
5 Slot G
6 CB when configuration includes TB
5. Parameters P918, U711 to U721 are not correctly set or not accepted after a change by means of U710 = 0 setting. (The meanings of these parameters are defined in the manual for the relevant CB board, see also function diagrams, Section 8, Sheets Z110 and Z111)
i015 Code number of board:
1. TB or 1st CB
2. 2 nd CB
6. The initialization run for a CB/TB board has not been completed within 40 s
i015 Code number of board:
1. TB or 1st CB
2. 2 nd CB