Forum
Share:
Notifications
Clear all
A01006 alarm in siemens 6RA80 DC Drive
1 Users
0 Reactions
Admin
Topic starter
(@click2electro)
Member
How can resolve problem A01006 alarm in siemens 6RA80 DC Drive ?
1 Reply
Admin
Topic starter
(@click2electro)
Member
Cause : Firmware update for DRIVE-CLiQ component required.
The firmware of a DRIVE-CLiQ component must be updated as there is no suitable firmware or firmware version in the component for operation with the Control Unit.
Alarm value (r2124, interpret decimal): Component number of the DRIVE-CLiQ component.
Remedy:
Firmware update using the commissioning software:
The firmware version of all of the components on the "Version overview" page can be read in the Project Navigator under "Configuration" of the associated drive unit and an appropriate firmware update can be carried out.
Firmware update via parameter:
- take the component number from the alarm value and enter into p7828.
- start the firmware download with p7829 = 1.
Reply