How can resolve problem A01045 alarm in siemens 6RA80 DC Drive ?
1 Reply
Jun 13, 2022 5:05 pm
Cause : CU: Configuring data invalid. An error was detected when evaluating the parameter files PSxxxyyy.ACX, PTxxxyyy.ACX, CAxxxyyy.ACX, or CCxxxyyy.ACX saved in the non-volatile memory.
Remedy:
Restore the factory setting using (p0976 = 1) and re-load the project to the drive unit. Operation without any restrictions is then possible.
After downloading the project, save the parameters in STARTER using "Copy RAM to ROM" or with p0977 = 1.
This overwrites the incorrect parameter files in the non-volatile memory.