Forum

Share:
Notifications
Clear all

A01069 alarm in siemens 6RA80 DC Drive

2 Posts
1 Users
0 Reactions
109 Views
Posts: 14967
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

How can resolve problem A01069 alarm in siemens 6RA80 DC Drive ?

1 Reply
Posts: 14967
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Parameter backup and device incompatible. The parameter backup on the memory card and the device type do not match (e.g. a memory card with the parameter backup of a SINAMICS S110 is inserted in SINAMICS DCM).

The module boots with the factory settings.

Remedy:

- insert a memory card with compatible parameter backup and carry out a POWER ON.
- insert a memory card without parameter backup and carry out a POWER ON.
- remove the memory card and carry out POWER ON.
- backup parameters (p0971=1).

Reply
Share: