A01100 alarm in siemens 6RA80 DC Drive

2 Posts
1 Users
0 Reactions
213 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem A01100 alarm in siemens 6RA80 DC Drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : CU: Memory card withdrawn. The memory card (non-volatile memory) was withdrawn during operation.

Notice: It is not permissible for the memory card to be withdrawn or inserted under voltage.

Remedy:

- power down the drive system.
- re-insert the memory card that was withdrawn - this card must match the drive system.
- power up the drive system again.

Reply