A01223 alarm in siemens 6RA80 DC Drive

2 Posts
1 Users
0 Reactions
174 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem A01223 alarm in siemens 6RA80 DC Drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : CU: Sampling time inconsistent - When changing a sampling time (p0115[0], p0799 or p4099), inconsistency between the clock cycles has been identified.

Alarm value (r2124, interpret decimal):
1: Value, low minimum value.
2: Value, high maximum value.
3: Value not a multiple of 1.25 μs.
4: Value does not match clock-cycle synchronous PROFIBUS operation.
5: Value not a multiple of 125 μs.
6: Value not a multiple of 250 μs.
7: Value not a multiple of 375 μs.
8: Value not a multiple of 400 μs.
10: Special restriction of the drive object violated.

Remedy:

- check the DRIVE-CLiQ cables.
- set a valid sampling time.
See also: p0115, p4099