Siemens 6RA80 DC Drive
2
Posts
1
Users
0
Reactions
157
Views
Jun 14, 2022 1:48 am
How can resolve problem A01224 alarm in siemens 6RA80 DC Drive ?
1 Reply
Jun 14, 2022 1:49 am
Cause : CU: Pulse frequency inconsistent - When changing the minimum pulse frequency (p0113) inconsistency between the pulse frequencies was identified.
Alarm value (r2124, interpret decimal):
1: Value, low minimum value.
2: Value, high maximum value.
3: Resulting sampling time is not a multiple of 1.25 μs.
4: Value does not match clock-cycle synchronous PROFIBUS operation.
10: Special restriction of the drive object violated.
99: Inconsistency of cross drive objects detected.
116: Recommended clock cycle in r0116[0...1].
Remedy: Set a valid pulse frequency.