How can resolve problem A01304 alarm in siemens 6RA80 DC Drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Firmware version of DRIVE-CLiQ component is not up-to-date. The non-volatile memory has a more recent firmware version than the one in the connected DRIVE-CLiQ component.

Remedy: Update the firmware (p7828, p7829 and commissioning software).