A01314 alarm in siemens 6RA80 DC Drive
1 Users
0 Reactions
Admin
Topic starter
(@click2electro)
Member
How can resolve problem A01314 alarm in siemens 6RA80 DC Drive ?
1 Reply
Admin
Topic starter
(@click2electro)
Member
Cause : Topology: Component must not be present. For a component, "de-activate and not present" is set but this component is still in the topology.
Alarm value (r2124, interpret hexadecimal):
ddccbbaa hex:
aa = component number
bb = component class of the component
cc = connection number
Note: Component class and connection number are described in F01375.
Remedy:
- remove the corresponding component.
- change the setting "de-activate and not present".
Note: Under "Topology --> Topology view" the commissioning software offers improved diagnostics capability (e.g. set- point/actual value comparison).
See also: p0105 (Activate/de-activate drive object), p0125 (Activate/de-activate power unit components), p0145 (Activate/de-activate encoder interface)