A01322 alarm in siemens 6RA80 DC Drive
1 Users
0 Reactions
Admin
Topic starter
(@click2electro)
Member
How can resolve problem A01322 alarm in siemens 6RA80 DC Drive ?
Admin
Topic starter
(@click2electro)
Member
Cause : Topology: Drive object number present twice in configuration. A drive object number is present more than once in p0978.
Alarm value (r2124, interpret decimal):
Index of p0978 under which the involved drive object number is located.
Remedy:
Set parameter p0009 = 1 and change p0978:
Rules:
- p0978 must include all of the drive object numbers (p0101).
- it is not permissible for a drive object number to be repeated.
- by entering a 0, the drive objects with PZD are separated from those without PZD.
- only 2 partial lists are permitted. After the second 0, all values must be 0.
- dummy drive object numbers (255) are only permitted in the first partial list.