How can resolve problem A01324 alarm in siemens 6RA80 DC Drive ?
1 Reply
Jun 14, 2022 5:24 am
Cause : Topology: Dummy drive object number incorrectly created. In p0978, dummy drive object numbers (255) are only permitted in the first partial list.
Remedy: Set p0009 to 1 and change p0978:
Rules:
- p0978 must include all of the drive object numbers (p0101).
- it is not permissible for a drive object number to be repeated.
- by entering a 0, the drive objects with PZD are separated from those without PZD.
- only 2 partial lists are permitted. After the second 0, all values must be 0.
- dummy drive object numbers (255) are only permitted in the first partial list.