Forum

Share:
Notifications
Clear all

A01382 fault in siemens 6RA80 DC Drive

1 Posts
1 Users
0 Reactions
5 Views
Posts: 17631
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Sensor Module incorrectly inserted comes when the topology comparison has detected a Sensor Module in the actual topology that has been incorrectly inserted with respect to the target technology.

A01382 fault in siemens 6RA80 DC Drive indicate Sensor Module incorrectly inserted. This means the drive system is no longer booted. In this state, the drive control (closed-loop) cannot be enabled.

  1. Insert the components involved at the right connection (correct the actual topology).
  2. Adapt the project/parameterization in the commissioning software (correct the target topology).
  3. Automatically remove the topology error (p9904).
Share: