Siemens 6RA80 DC Drive
1
Posts
1
Users
0
Reactions
49
Views
Sep 21, 2024 4:42 am
Cause : Terminal Module incorrectly inserted comes when the topology comparison has detected a Terminal Module in the actual topology that has been incorrectly inserted with respect to the target technology.
- Insert the components involved at the right connection (correct the actual topology).
- Adapt the project/parameterization in the commissioning software (correct the target topology).
- Automatically remove the topology error (p9904).