A01385 fault in siemens 6RA80 DC Drive indicate that the Controller Extension incorrectly inserted. This means he topology comparison has detected a controller extension 32 (CX32) in the actual topology that has been incorrectly inserted with respect to the target topology.
- Insert the components involved at the right connection (correct the actual topology).
- Adapt the project/parameterization in the commissioning software (correct the target topology).
- Automatically remove the topology error (p9904).