Siemens 6RA80 DC Drive
1
Posts
1
Users
0
Reactions
42
Views
Sep 21, 2024 4:56 am
A01481 fault in siemens 6RA80 DC Drive indicate that the power unit not inserted. This means the topology comparison has detected a power unit that is missing in the actual topology with respect to the target topology.
- Insert the components involved at the right connection (correct the actual topology).
- Adapt the project/parameterization in the commissioning software (correct the target topology).
- Check the 24 V supply voltage.
- Check DRIVE-CLiQ cables for interruption and contact problems.
- Check that the component is working properly.