A01911 alarm in siemens 6RA80 DC Drive indicate that the clock cycle synchronous operation clock cycle failure. This means the global control telegram to synchronize the clock cycles has failed - in cyclic operation - for several DP clock cycles or has violated the time grid specified in the parameterizing telegram over several consecutive DP clock cycles.
- Check the physical bus configuration (cable, connector, terminating resistor, shielding, etc.).
- Check whether communication was briefly or permanently interrupted.
- Check the bus and controller for utilization level (e.g. bus cycle time Tdp was set too short).