Forum

Share:
Notifications
Clear all

A02020 alarm in siemens 6RA80 DC Drive

1 Posts
1 Users
0 Reactions
9 Views
Posts: 17739
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

A02020 alarm in siemens 6RA80 DC Drive indicate that the Parameter cannot be changed. This means this parameter setting cannot be changed when the function generator is active (p4800 = 1).

  1. See also: p4810, p4812, p4813, p4820, p4821, p4822, p4823, p4824, p4825, p4826, p4827, p4828, p4829
  2. Stop the function generator before parameterizing (p4800 = 0).
  3. If required, start the function generator (p4800 = 1).
Share: