A02099 alarm in siemens 6RA80 DC Drive indicate that the Insufficient Control Unit memory. This means the memory space still available on the Control Unit is no longer sufficient for the trace function.
Reduce the memory required, e.g. as follows:
- reduce the trace time.
- increase the trace clock cycle.
- reduce the number of signals to be traced.