Forum

Share:
Notifications
Clear all

A07448 alarm in siemens 6RA80 DC Drive

1 Posts
1 Users
0 Reactions
44 Views
Posts: 18163
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

A07448 alarm in siemens 6RA80 DC Drive indicate that the Position tracking, linear axis has exceeded the maximum range. This means a configured linear axis/no modulo axis, the currently effective motor encoder (encoder 1) has exceeded the maximum possible traversing range.

The fault should be resolved as follows:

1. Select encoder commissioning (p0010 = 4).
2. Reset position tracking, position (p2720.2 = 1).
3. De-select encoder commissioning (p0010 = 0).

Share: