A07552 alarm in siemens 6RA80 DC Drive
1 Users
0 Reactions
Admin
Topic starter
(@click2electro)
Member
A07552 alarm in siemens 6RA80 DC Drive indicate that the Encoder configuration not supported. This means the requested encoder configuration is not supported. Only bits may be requested in p0404 that are signaled as being supported by the encoder evaluation in r0456.
  1. Check the encoder parameterization (p0400, p0404).
  2. Use the matching encoder evaluation (r0456).