A08526 alarm in siemens 6RA80 DC Drive indicate No cyclic connection. This means there is no cyclic connection to the control.
- Establish the cyclic connection and activate the control with cyclic operation.
- For PROFINET, check the parameters "Name of Station" and "IP of Station" (r61000, r61001).
- If a CBE20 is inserted and PROFIBUS is to communicate via PZD Interface 1, then this must be parameterized using the STARTER commissioning tool or directly using p8839.