A30033 alarm in siemens 6RA80 DC Drive indicate that the hardware current limit for phase W responded. The pulsing in this phase is inhibited for one pulse period.
  1. Check the motor circuit configuration (star/delta).
  2. Check the motor load.
  3. Check the power cable connections.
  4. Check the power cables for short-circuit or ground fault.
  5. Check the length of the power cables.